--- In "Breton M. Saunders"
<> wrote:
>
> Quick question r/e CPLD register addresses on the ts-7400:
>
> Are they all byte only registers? For example, if I do a
> readl(0x12c00000) will I get the contents of all four addresses
(0x12c0
> 0000, ..1, ..2, ..3) or must I readb on each one?
Those registers at 0x12c00000 will work this way. The CPU will break
up the 32 bit access to 4 8bit reads and the bus cycle will take 4
times as long. The only difference between reading the regs this way
and using 4 individual byte loads is that the read strobe will be
asserted for the entire (4x longer) bus cycle. Those registers have
a 100% combinational data path from the address lines to the data bus
so they're ok. The UART registers don't work that way however, so
you can't just do a single 16-bit read and expect to get both
registers in one cycle for those. Most all other CPLD registers will
behave as you expect for >8bit reads though.
>
> Same question applies for writes.
>
> I know that the EEPROM chip select register (0x2300_0000) only
works if
> I perform byte wide reads/writes on it.
Be careful with writes. The way the 0x2300_0000 address is decoded,
it is aliased. i.e. 0x2300_0001, 0x2300_0002, and 0x2300_0003 are
all the same register. When you write the 32-bit value 0x12345678,
the CPU will break down the 32-bit cycle into 4 8-bit cycles and
execute them LSB first. The last write will be 0x12 to address
0x2300_0003 and will be what you end up writing to the register.
Your safest course of action is to only use 8-bit reads on CPLD
registers. (strb, ldrb arm insns)
//Jesse Off
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/ts-7000/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/ts-7000/join
(Yahoo! ID required)
<*> To change settings via email:
<*> To unsubscribe from this group, send an email to:
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/
|