--- In  "mccarl1978" <> wrote:
>
> 
> 
> --- In  "j.chitte" <j.chitte@> wrote:
> >
> > Hi,
> > 
> > I'm using an LED as a light sensor. It is shunted by 200k and buffered by a 
> > voltage follower, then sampled by the MAX197 on the 7250. The follower has 
> > a 2k pull down resistor since the op-amp can't sink enough current at 
> > outputs near the 0V rail.
> 
> Why do you say that the op-amp can't "sink" enough current near 0V? It 
> doesn't sound like the output is going negative. If the voltage is still 
> positive (even if only small) then it is still "sourcing" current. You 
> shouldn't need any "pull-down" resistor at all. All you are doing is further 
> loading the op-amp. ie. The load on the op-amp from just the MAX197 is 
> normally 16k/21k depending on bi/unipolar mode, but with the resistor you 
> speak of, the load is increasing to approx 2k.
> 
> 
> > 
> > All other channels seem to sample correctly but don't sample this low. This 
> > one seems to need double read on low voltages.
> > 
> > Subsequent samplings seem correct but after delay of about a minute the 
> > initial reading is at or near zero.
> > 
> > $ ./adc_logger -c 4 3,0 && sleep 15 && ./adc_logger -c 4 3,0
> > # ch3
> > 
> > 0.071 
> > 0.067 
> > 0.071 
> > 0.067 
> > # ch3
> > 
> > 0.068 
> > 0.070 
> > 0.000 
> > 0.070 
> > $ ./adc_logger -c 4 3,0 && sleep 60 && ./adc_logger -c 4 3,0
> > # ch3
> > 
> > 0.072 
> > 0.070 
> > 0.071 
> > 0.071 
> > # ch3
> > 
> > 0.002 
> > 0.071 
> > 0.072 
> > 0.076 
> > 
> > Testing the input to the follower shows the expected final value and is 
> > constant.
> > 
> > I'm having a bit of difficulty seeing what may be happening, any ideas?
> > 
> > TIA.
> >
>

Hi,

these op-amps have an output swing from low rail to high rail - 1.5V. Sort of 
half R2R. At they can source 40mA but only sync 40uA. 

If I understand the MAX197 in unipolar mode (I'm using 0-5V) it does an 
internal offset. The input is floating arount 2.5V . If I feed a signal of 0.5V 
that means my op-amp needs to sink 2/20k= 100uA.

Is that incorrect?

thanks for your reply.




------------------------------------

Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/ts-7000/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/ts-7000/join
    (Yahoo! ID required)

<*> To change settings via email:
     
    

<*> To unsubscribe from this group, send an email to:
    

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/

<Prev in Thread] Current Thread [Next in Thread>
Admin

Disclaimer: Neither Andrew Taylor nor the University of NSW School of Computer and Engineering take any responsibility for the contents of this archive. It is purely a compilation of material sent by many people to the birding-aus mailing list. It has not been checked for accuracy nor its content verified in any way. If you wish to get material removed from the archive or have other queries about the archive e-mail Andrew Taylor at this address: andrewt@cse.unsw.EDU.AU